Default Hold-up time explained

Yeah another topic about the hold-up time. Why? Because I got the feeling some really don't understand what it is, what it does and what the problem is.

What is the hold-up time?
It's the time in milliseconds that the PSU can work without without getting any power, measured at full load.

How does it work?
The primary capacitor of the PSU can store enough energy for the PSU to work some milliseconds after the power is cut.

How long should it last?
According to the ATX specification the PSU should deliver at least 17ms full power with voltages still inside the ATX spec.

But at least 1ms before the output voltages of the PSU go out of spec the PSU should drop the Power OK signal.

Power OK signal?
Yes Power OK signal, that's a wire in the 24 pins ATX connector that tells the motherboard that the power of the PSU is stable and that the PC can start or should shutdown.

What's the problem then?
Some PSU don't drop the Power OK before the output voltages of the PSU go out of spec. This isn't good because it puts a lot of stress on the components of the PC that are powered by the PSU and now getting voltages that are outside of spec.

Is it really a problem?
Well that depends if you experience a lot of problems with power outage where you life, it could be a problem. But if that is the case a UPS is maybe something that you should buy.

But there is something else you should know!
Hold-up time is measured at full load! Almost no one loads his of her PSU till full load. And even if someone does, the chance that PSU is working at full load if the power fails, is almost zero.

So that means that hold-up time actually should last a lot longer in real life conditions. It even could mean that the power OK signal drops before the output voltages go out of spec.

So it actually isn't a problem?
For most people not no.

So please don't make this a huge problem, because it isn't one. It simply isn't done right according to the ATX specification.

For more information and tests see the reviews from Aris on TechPowerUp and TomsHardware:
http://www.techpowerup.com/reviews/?...=25&order=date
http://www.tomshardware.com/articles...power-supplies

Last edited by -The_Mask-; 05-05-2016 at 06:17 AM.
Reply With Quote
The Following 11 Users Say Thank You to -The_Mask- For This Useful Post:
Chipskate (05-05-2016), cypherpunks (12-20-2016), ehume (05-06-2016), Evilution (05-25-2016), GDILord (05-24-2016), jonnyGURU (05-05-2016), marcos669 (05-05-2016), marctronixx (12-23-2016), none77 (05-06-2016), sblantipodi (03-17-2017), sith'ari (05-05-2016)
  #2  
Old 05-05-2016
marcos669 marcos669 is offline
200W User
 
Join Date: Mar 2016
Location: Spain
Posts: 25
Thanks: 1
Thanked 0 Times in 0 Posts
Default

Great and straight to the point info, I looked for something like this a few days ago but couldn´t find much
Reply With Quote
  #3  
Old 05-05-2016
GI_Joe GI_Joe is offline
Antec Rep
 
Join Date: Dec 2007
Posts: 558
Thanks: 57
Thanked 132 Times in 89 Posts
Default

Your PG stuff is wrong. Will explain tomorrow.
Reply With Quote
  #4  
Old 05-05-2016
Philipus II's Avatar
Philipus II Philipus II is offline
retired reviewer
 
Join Date: Jul 2011
Location: Germany, Berlin
Posts: 1,453
Thanks: 766
Thanked 349 Times in 227 Posts
Default

Here in Germany hold up time is only relevant for professional use. I don't remember any power loss in the last two years here in my flat. In other countries power losses are normal. In my 6 month in spain the power was out at least once per month.
Reply With Quote
The Following User Says Thank You to Philipus II For This Useful Post:
sith'ari (05-06-2016)
  #5  
Old 05-05-2016
sith'ari sith'ari is offline
Flux Capacitor User
 
Join Date: Oct 2014
Location: Emperor's Retreat/Naboo Moenia
Posts: 869
Thanks: 1,418
Thanked 205 Times in 126 Posts
Default

Quote:
Originally Posted by -The_Mask- View Post
.
.
.
So that means that hold-up time actually could last a lot longer in real life conditions. It even could mean that the power OK signal drops before the output voltages go out of spec.
The magic word is "could".
"Could" doesn't specify certainty. "Could" means that either it will or it will not !!
And as i said multiple times in the past, i'm not a person that likes risks, and the 50%-50% chance of the "could" word, is a serious risk percentage in my opinion.
So, if it 1) "could mean that the power OK signal drops before the output voltages go out of spec.", it also 2) could mean that the Power_OK could drop much much later after the voltages get out of spec!!!
So the conclusion is that we need even more thorough testing and NOT to abandon them completely and pretend that the issue doesn't exist at all !!!
__________________
CPU:Athlon 64 FX60 (2-cores) 2,6GHz
Mobo:Asrock 939a785g
cpu cooler:ArcticFreezer13 CO
RAM:4 GB DDR 400MHz
GPU:Asus 750 Ti 2GB
PSU:Seasonic Platinum 660
Monitor:Asus VE228HR
Tower:Coolermaster Elite 430
Reply With Quote
  #6  
Old 05-05-2016
-The_Mask-'s Avatar
-The_Mask- -The_Mask- is offline
ssssssmokin'
 
Join Date: Jun 2010
Location: The Netherlands
Posts: 4,565
Thanks: 328
Thanked 1,275 Times in 836 Posts
Default

Quote:
Originally Posted by sith'ari View Post
The magic word is "could".
Changed the first could to should.

Quote:
and the 50%-50% chance of the "could" word, is a serious risk percentage in my opinion.
As I was trying to explain, the chance is probably very small in real life.
Reply With Quote
The Following User Says Thank You to -The_Mask- For This Useful Post:
sith'ari (05-05-2016)
  #7  
Old 05-05-2016
quest for silence's Avatar
quest for silence quest for silence is offline
Silencer & heathen relic of a human (™ by OW)
 
Join Date: Sep 2013
Location: Italy
Posts: 3,353
Thanks: 1,037
Thanked 486 Times in 421 Posts
Default

Quote:
Originally Posted by -The_Mask- View Post
Some PSU don't drop the Power OK before the output voltages of the PSU go out of spec.
And why then UVP doesn't kick in, in that case? Is it too slow?


Quote:
Originally Posted by Philipus II View Post
In other countries power losses are normal. In my 6 month in spain the power was out at least once per month.
Italy is much more similar to Spain.
__________________
Best, Luca
Reply With Quote
  #8  
Old 05-05-2016
-The_Mask-'s Avatar
-The_Mask- -The_Mask- is offline
ssssssmokin'
 
Join Date: Jun 2010
Location: The Netherlands
Posts: 4,565
Thanks: 328
Thanked 1,275 Times in 836 Posts
Default

Quote:
Originally Posted by quest for silence View Post
And why then UVP doesn't kick in, in that case? Is it too slow?
UVP is mostly set to kick in by a much bigger drop.
Quote:
Italy is much more similar to Spain.
The Netherlands is more like Germany, it almost never happens.
Reply With Quote
  #9  
Old 05-05-2016
sith'ari sith'ari is offline
Flux Capacitor User
 
Join Date: Oct 2014
Location: Emperor's Retreat/Naboo Moenia
Posts: 869
Thanks: 1,418
Thanked 205 Times in 126 Posts
Default

Quote:
Originally Posted by -The_Mask- View Post
Changed the first could to should.
As I was trying to explain, the chance is probably very small in real life.
Oh come on.....!!!
I can't resist with what you are writing!!! Again, probably doesn't specify certainty, and i'm not a person that likes risks and ....blah blah blah you know the rest !!!
__________________
CPU:Athlon 64 FX60 (2-cores) 2,6GHz
Mobo:Asrock 939a785g
cpu cooler:ArcticFreezer13 CO
RAM:4 GB DDR 400MHz
GPU:Asus 750 Ti 2GB
PSU:Seasonic Platinum 660
Monitor:Asus VE228HR
Tower:Coolermaster Elite 430
Reply With Quote
  #10  
Old 05-05-2016
quest for silence's Avatar
quest for silence quest for silence is offline
Silencer & heathen relic of a human (™ by OW)
 
Join Date: Sep 2013
Location: Italy
Posts: 3,353
Thanks: 1,037
Thanked 486 Times in 421 Posts
Default

Quote:
Originally Posted by -The_Mask- View Post
UVP is mostly set to kick in by a much bigger drop.
1.2V are not enough? So which is the (general) UVP usefulness/goal?


Quote:
Originally Posted by -The_Mask- View Post
The Netherlands is more like Germany, it almost never happens.
Pares cum paribus facillime congregantur.
__________________
Best, Luca
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -4. The time now is 03:41 PM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2018, vBulletin Solutions, Inc.
Copyright © JonnyGURU.com 2000 -